Odd question here - I've been asked to provide the maximum live load an existing mezzanine inside of a PEMB can support using the 2012 IBC. The mezzanine is actually an interior build out that creates some offices and meeting spaces. The mezzanine is the area above these spaces. The walls are all wood 2x4 and the mezzanine framing is what appears to be 1000s162-54 CFS joists. Based on the existing bearing wall locations and assuming a simple span I get that these are good for about 60 psf of live load.
So here is the tricky part - this building is being used as a dog training facility and they want to use the mezzanine as some light storage and part of the mezzanine will have what they are calling a "puppy play" area. Basically, a room where they will have some training classes for puppies. What live is this? Safe to assume just classroom loading (40 psf) for the puppy play area and storage area above ceilings for the storage (20 psf)? I know the commentary for ASCE 7-10 has a live load for a nonresidential attic (see table C4-1) but I'm not sure what the differentiating factor would be.
Thoughts?
So here is the tricky part - this building is being used as a dog training facility and they want to use the mezzanine as some light storage and part of the mezzanine will have what they are calling a "puppy play" area. Basically, a room where they will have some training classes for puppies. What live is this? Safe to assume just classroom loading (40 psf) for the puppy play area and storage area above ceilings for the storage (20 psf)? I know the commentary for ASCE 7-10 has a live load for a nonresidential attic (see table C4-1) but I'm not sure what the differentiating factor would be.
Thoughts?