CURVEB
Structural
- Jul 29, 2013
- 133
In the IBC 2015 table 1607.1, what is the purpose of footnote 'm' on live loads of 100 psf or less? We are having some internal discussions about whether or not you can reduce these loads. Although footnote m states that these loads cannot be reduced, it goes on to say "unless specific exceptions of 1607.10 apply".
We read 1607.10.2 #1 to say that live loads of 100 psf or less may be reduced.
In other words, if we have an occupancy of Residential/Public Rooms, the Lo is 100 psf. It cannot be reduced by footnote m, but if you use section 1607.10.2, it allows reductions in live loads of 100 psf or less.
The previous iterations of the IBC had an exception that Group A assembly occupancies could not be reduced, but we always interpreted that to only apply to loads under the "Assembly" area of table 1607.1. The 100 psf loads that show up under other primary occupancies could still be reduced as long as the other exceptions are met.
Any thoughts or different interpretations?
We read 1607.10.2 #1 to say that live loads of 100 psf or less may be reduced.
In other words, if we have an occupancy of Residential/Public Rooms, the Lo is 100 psf. It cannot be reduced by footnote m, but if you use section 1607.10.2, it allows reductions in live loads of 100 psf or less.
The previous iterations of the IBC had an exception that Group A assembly occupancies could not be reduced, but we always interpreted that to only apply to loads under the "Assembly" area of table 1607.1. The 100 psf loads that show up under other primary occupancies could still be reduced as long as the other exceptions are met.
Any thoughts or different interpretations?