I wanted to get some input on some live loads which are not specifically addressed in ASCE-7 (05)
Dorm rooms: 40 psf (Hotel-private room)+ 10 psf for good measure =50
Student lounge in a dorm building: 50 psf (same as dorm room) or should it be higher.
Conference room: Office area live load of 50 psf.
Trash collection area in a student building: 125 psf (light storage)