Hello
I have ben doing power calcs for some years off and on. Recently I joined a new company and I came across the way these folks do the calculations. And they are convincing me to do it their way. Much against my intuition.
Here is the story:
case 1
transformer secondary DELTA 208V
Feeds following loads
3 phase 208V 15Amps VA = 5404
3 phase 208V 20 Amps va=7205
3 phase 208V 18 Amps va=6484
1 phase 208V 10 amps va= 2080
1 phase 208v 15 amps va= 3120
1 phase 208v 20 amps va=4160
My calcs:
Total VA = 28453
Line current = 80 amps
CURRENT DISTRIBUTION BETWEEN PHASES:
15 15 15
20 20 20
18 18 18
10 10
15 15
20 20
TOT 98 78 68
MAIN CIRCUIT BREAKER RATING 100 AMPS
PANEL RATING 125 AMPS
My companys method: Multiply 98 x 1.732 = 170
78 x 1.732 = 135
68 x 1.732 = 118
SIZE CIRCUIT BREAKER FOR 170 AMPS. (His Line current)
This must be wrong ?? My managers solution
What if the transformer secondary is Y instead of delta.?
he says that is because the phase current x 1.73 = line current
My response: Wether it is y or Delta secondary, the following is still true:
MAIN CIRCUIT BREAKER RATING 100 AMPS
PANEL RATING 125 AMPS
He likes 170 Amps. Who is correct?
Thanks.
I have ben doing power calcs for some years off and on. Recently I joined a new company and I came across the way these folks do the calculations. And they are convincing me to do it their way. Much against my intuition.
Here is the story:
case 1
transformer secondary DELTA 208V
Feeds following loads
3 phase 208V 15Amps VA = 5404
3 phase 208V 20 Amps va=7205
3 phase 208V 18 Amps va=6484
1 phase 208V 10 amps va= 2080
1 phase 208v 15 amps va= 3120
1 phase 208v 20 amps va=4160
My calcs:
Total VA = 28453
Line current = 80 amps
CURRENT DISTRIBUTION BETWEEN PHASES:
15 15 15
20 20 20
18 18 18
10 10
15 15
20 20
TOT 98 78 68
MAIN CIRCUIT BREAKER RATING 100 AMPS
PANEL RATING 125 AMPS
My companys method: Multiply 98 x 1.732 = 170
78 x 1.732 = 135
68 x 1.732 = 118
SIZE CIRCUIT BREAKER FOR 170 AMPS. (His Line current)
This must be wrong ?? My managers solution
What if the transformer secondary is Y instead of delta.?
he says that is because the phase current x 1.73 = line current
My response: Wether it is y or Delta secondary, the following is still true:
MAIN CIRCUIT BREAKER RATING 100 AMPS
PANEL RATING 125 AMPS
He likes 170 Amps. Who is correct?
Thanks.