We have a client for whom we provide stamping of drawings for ballasted solar panel mounting systems. Checking the structural capacity of the actual flat rooftop is by others, usually (strictly speaking, we're not a structural firm, though as a geotech oriented outfit we do a lot of structural design work for buried structures per AASHTO, but never IBC).
One of this client's clients is asking us to check the structural capacity of a rooftop for one of the arrays. I looked in 2009 IBC, and the minimum point load carrying capacity for design seems to be 300 lbs. The loads for the system per ASCE 7 seem to break down thusly:
D = 68 lbs ballast + gravel + decking
L = ??? (I assume this is in IBC somewhere but I'm wondering if it should be zero since nobody is going to be walking on top of the solar panels)
S = 20 psf X 17.6 SF panel = 352 lb point load
W = 16 psf X 17.6 SF (roughly - need to check this)
The worst case load combo seems to be #3:
1.5D + 1.6S + 0.5W =
1.2(68 lb) + 1.6(352 lb) + 0.5(281.6) = 806 lbf
And that doesn't even include the gravel portion of dead load.
What I'm wondering is two things:
1. Am I doing this correctly, and
2. Is there any chance that this roof is going to be able to carry this point load? Should we even go to the effort? Assuming it was designed per 2009 IBC, it was only required to carry 300 lbs. Is the point load carrying capacity usually a controlling design consideration for a steel truss roof with metal decking and gravel? Or is there usually a lot of excess point load carrying capacity?
One of this client's clients is asking us to check the structural capacity of a rooftop for one of the arrays. I looked in 2009 IBC, and the minimum point load carrying capacity for design seems to be 300 lbs. The loads for the system per ASCE 7 seem to break down thusly:
D = 68 lbs ballast + gravel + decking
L = ??? (I assume this is in IBC somewhere but I'm wondering if it should be zero since nobody is going to be walking on top of the solar panels)
S = 20 psf X 17.6 SF panel = 352 lb point load
W = 16 psf X 17.6 SF (roughly - need to check this)
The worst case load combo seems to be #3:
1.5D + 1.6S + 0.5W =
1.2(68 lb) + 1.6(352 lb) + 0.5(281.6) = 806 lbf
And that doesn't even include the gravel portion of dead load.
What I'm wondering is two things:
1. Am I doing this correctly, and
2. Is there any chance that this roof is going to be able to carry this point load? Should we even go to the effort? Assuming it was designed per 2009 IBC, it was only required to carry 300 lbs. Is the point load carrying capacity usually a controlling design consideration for a steel truss roof with metal decking and gravel? Or is there usually a lot of excess point load carrying capacity?