Load factors in ACI 318 1971 1

Status
Not open for further replies.

dcceecy

Structural
Oct 15, 2008
112
we are checking a concrete floor built in 1974.
The current load combination is 1.2DL+1.6LL from ACI 318.
I am wondering what they used in 1974. 1.4DL+1.7LL?
we do no have a copy for ACI318 1971. Can anyone help me out?
Thanks.
 
Replies continue below

Recommended for you

I have ACI 318-63 but I don't know if that would have still been in effect in 1974. It specified:

U = 1.5D + 1.8L
or
U = 1.25(D + L + W)
or
U = 0.9D + 1.1W

BA
 
I believe you can purchase ACI 318-71 online for $25.

BA
 
Be aware that some of the capacity reduction factors may have changed as well.
 
If you can wait until Wednesday, I have ACI 318-71 in my office. But I'm on vacation now.
 
JedClampett
Thank you. Please let us know the load factors and the reduction factor of ACI 318 1971
 
I did some research online and found a paper talking about the load reduction factors of earlier days.
Please see the attached pdf.
According to the paper (to calculate the overall or global factor of safety, line 12-18), we can solve these two equations to find the load factors
a*D+b*D (=L) = 1.72*0.9*2*D
a*D+b*D/2 (=L) = 1.67*0.9*1.5*D

then a=1.4, b=1.7

Somebody please verify those load factors if you have ACI318 1971. Thanks.
 
 http://files.engineering.com/getfile.aspx?folder=05bc545f-c942-4ef8-9d3c-b53b84c9edca&file=ACI_318_1971_load_combination.pdf
Thank you for the verification.
I am very curious now. why are those load factors used in cocnrete (in such earlier days) while ASD were used for almost all other materails?
Does that come from a tradition or the ACI 318 committee just adopted some research paper using load factors? Does anybody know the particular reason?
Sorry, too many questions.

Thanks.
 
My guess is that the failure mechanisms of concrete used with LRFD were:
1) Easier to calculate
2) Easier to match with test data
3) Someone had to be first.
 