Load from a fan

Status
Not open for further replies.

dlasalle

Structural
Mar 27, 2023
2
I've got a fan pushing air at 40mph at a vertical plate. Wondering what the best way to calculate that load is. Current method is using ASCE7 wind load formula with K[sub]d[/sub] & G as 1.0. Is this the best method or is there another I'm unaware of?
 
Replies continue below

Recommended for you

What is the size and material of the plate? Is it safe to assume that this plate and fan system are occurring in the interior of a building or is the plate located at the exterior face of the building?
 
If the dimensions of the vertical plate are several feel in each dimension, I'd consider ASCE 7 freestanding walls to apply nicely.
 
dlasalle said:
...fan pushing air at 40mph at a vertical plate.

That's "dynamic pressure" from a moving fluid.
In imperial units:

Pressure (lb/ft[sup]2[/sup]) = 0.5 x air density (slugs/ft[sup]3[/sup]) x [air velocity (ft/sec)][sup]2[/sup]

Air density depends primarily on altitude.

 