Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Load Requirements for Catwalks 5

Status
Not open for further replies.

sigma1

Structural
Jun 26, 2003
105
US
Any information regarding loading requirements for catwalks will be appreciated.
 
Replies continue below

Recommended for you

What application?

Check the building codes, OSHA, perhaps other industry standards as applicable.
 
That being for "Assembly areas and Theaters" in my 2003 IBC. But I've seen "catwalk" used in pretty generic ways, as in industrial applications.
 
It is for an Assembly area/Theater and it is adequate for up to 100 psf.

Thanks everyone
 
Big difference between industrial, commercial and public use catwalks. If in a theater and the catwalk could be loaded up with groupies, cast or crew then 40psf or even 100 psf may be light. Adding a few pounds or even tons of steel is small compared to the issues if a failure occurs and people are hurt.
 
NO GROUPIES. It is for a School with very little acces to anyone other than the maintainance people. The architect did not even want a guardrail but we provided one.

Thanks for the warning.
 
You may be (mildly) interested to know that on this side of the Atlantic, the British Standard specifies not a udl but a series of point loads on a cat-walk of 1kN (approx 220lb) at 1m centres.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top