tyboy
Electrical
- Dec 20, 2002
- 8
I have 3 Solar Taurus 60 turbines driving 4160 vac 4.75 KW generators and am having load sharing problems.I can share load with the B & C machines but cannot load share the A& C machines without getting into a reverse power condition.I have checked wiring from Allen-Bradley Load share modules and is wired accordingly.The only thing I am not sure of is the wiring (polarity) of the CT's as this was done by a contractor.Can anyone else out there suggest something I may be missing?