Involved in an interesting situation.
On a few of the jobs we are working on there are existing stairway/walkway platforms that had been installed. We had been asked if we could add some load to the walkway platforms (piping/electrical conduit). So we analyzed the bracket supporting the platform and determined it didn't meet code requirements. We had an initial conversation with the manufacturer and they sent us what I'd call a "napkin calc" showing the stress in the angle of approximately 26 ksi. This exceeds the allowable stress of 24 ksi.
So, we developed a detailed calc package using AISC equations that showed an overstress of approximately 60% and sent this to them. They didn't didn't provide any calculations back, but provided some load test results.
I can't seem to find much info or requirements on load testing. Are there any standards? If a structure is required to carry 2 kip per code and the load test proves it can carry that 2 kip is that acceptable or is there a factor of safety that must be applied?
There is no doubt in my mind that the bracket doesn't meet the theoretical code requirements (AISC), but is it possible to circumvent that by doing a load test?
On a few of the jobs we are working on there are existing stairway/walkway platforms that had been installed. We had been asked if we could add some load to the walkway platforms (piping/electrical conduit). So we analyzed the bracket supporting the platform and determined it didn't meet code requirements. We had an initial conversation with the manufacturer and they sent us what I'd call a "napkin calc" showing the stress in the angle of approximately 26 ksi. This exceeds the allowable stress of 24 ksi.
So, we developed a detailed calc package using AISC equations that showed an overstress of approximately 60% and sent this to them. They didn't didn't provide any calculations back, but provided some load test results.
I can't seem to find much info or requirements on load testing. Are there any standards? If a structure is required to carry 2 kip per code and the load test proves it can carry that 2 kip is that acceptable or is there a factor of safety that must be applied?
There is no doubt in my mind that the bracket doesn't meet the theoretical code requirements (AISC), but is it possible to circumvent that by doing a load test?