katwalatapan
Electrical
- Aug 9, 2011
- 153
Hello,
The electrical mains at one of the facility that I'm looking at is rated at 225A, 3-phase, 120/240V. I couldn't find the plans for it, so I'm assuming it to be delta configuration, which then essentially allows 1-phase(neutral) 120V, 2-phase 240V, 1-phase(high leg-neutral) 280V, and 3-phase 240V.
I wanted to inquire if a load rated at 3-phase 208V could be served using the available 3-phase 240V? I understand if the service is 3-phase 208V and if the load is 3-phase 240V, it would cause overheating of the equipment, so would it be true the other way round?
Thank you.