Local Exhaust Ventilation

Status
Not open for further replies.

saumian

Chemical
Jul 1, 2003
20
0
0
CA
We transfer a ammonia solution from Bulk-Trailer to a 6000 gal bulk-storage tank which is located inside our facility. This solution has 25% ammoniam hydroxide, 25% ammoniam chloride, and the rest is water and some other minor components. The transfer rate is 70 gal/min. What is the proper way to get rid of ammonia vapors coming into the facility?

 
Replies continue below

Recommended for you

Saumian

Consider routing the tank vent to a spray scrubber to clean the air that is displaced by the incoming liquid. Ammonia vapours are effectively scrubbed with a dilute acid solution (e.g. sulfuric acid).

PeterAB.
 
I assume the ammonia leaves your bulk storage tank via the "breather" as displaced air.

A very simple "bubble" chamber attached to the breather (together with a vacuum relief valve) containing dilute sulphuric acid will do the trick.

Be careful of the depth of immersion of the chamber inlet. If the tank is rated to say 4 inch WG, then don't submerge the inlet pipe further than say 3 inches.

Profaic
 
bobhearn11 solution is best. This practice is done at many facilities where fugitive emission is to be controlled during transfer.
 
Is your ammonia odor problem caused whilst the disconnecting the transfer hose ?

If this is the case - use ECOSORB Odor Neutralizer (713 910 3773) which neutralizes Ammonia odors on contact, without the use of hazardous chemicals (sulphuric acid, etc.). It is a safe, cost effective solution which is only used when the spill odor occurs.

Allen Botha
 