Hello,
I am confused in selecting the required water supply demand and standpipe locations for firefighting system in a building. Building is partially sprinklered; 2 car parks and 3 commercial floors, remaining non-sprinklered are 7 residential floors. Occupancy is light and ordinary hazard 1.
Building has 6 stairways in total but 4 of them are emergency. Architectural layout is attached. I plan to use combined sprinkler system Class I using pipe calculation method.
1. Does all 6 stairways require standpipes? or I can use 4 stairways (which are circled in the attached layout). NFPA states that every stairway requires a standpipe, but thats only about emergency exits I guess. If I use the 4 standpipes, I do not need additional fire hose cabinets inside the building as 150 ft and 200 ft travel distances can be met using 4. However, these stairways start from the Ground floor till roof. The other 2 stairways (at the top side of building) run through all basements till roof.
2. Along with Q.1 as stated above, is there any other location(s) too which I must consider for FHCs or standpipes? What about the Entrance? (I read the section but did not get a clear picture of what NFPA wants)
3. Can I use 1250gpm pump for this arrangement (max. acc to NFPA 13) of 4 standpipes or I have to add 500gpm (for ordinary hazard, partially sprinklered buildings) to this? Wont 1750 gpm be too big for this scale of building?
3. Using 1250 gpm pump on the underground water tank, I plan on taking 8in main header/supply pipe and extract 6in standpipes from the main on required locations. Is it fine? If I have to use 1750gpm, how much should I increase the pipe sizes?
4. Building total elevation is approx. 150ft. Hence using 1250GPM and setting 120psi at the top most 2 1/2" valve of the remotest riser and using 500gpm for that riser to calculate friction losses plus the friction loss in the 8in main pipe, I get a required pump head of approx. 460'. Is this approach OK?
5. Using 460' pump head, I will have to install a pressure regulator on sprinkler pipe take off at only 1 floor to reduce pressure to lesser than 175 psi in the sprinkler system. But, if I set 100 psi instead of 120 psi at the top, I wont even have to use this regulator, but I used 120 psi to be on safer side. What do you suggest?
6. Lastly, 100 psi min. requirement is at the valve or end of hose pipe (at nozzle)? As I read somewhere, a 150ft hose pipe also induces considerable pressure loss should it be considered while doing pump head calculations?
Thanks in advance for all the help you people can give.
I am confused in selecting the required water supply demand and standpipe locations for firefighting system in a building. Building is partially sprinklered; 2 car parks and 3 commercial floors, remaining non-sprinklered are 7 residential floors. Occupancy is light and ordinary hazard 1.
Building has 6 stairways in total but 4 of them are emergency. Architectural layout is attached. I plan to use combined sprinkler system Class I using pipe calculation method.
1. Does all 6 stairways require standpipes? or I can use 4 stairways (which are circled in the attached layout). NFPA states that every stairway requires a standpipe, but thats only about emergency exits I guess. If I use the 4 standpipes, I do not need additional fire hose cabinets inside the building as 150 ft and 200 ft travel distances can be met using 4. However, these stairways start from the Ground floor till roof. The other 2 stairways (at the top side of building) run through all basements till roof.
2. Along with Q.1 as stated above, is there any other location(s) too which I must consider for FHCs or standpipes? What about the Entrance? (I read the section but did not get a clear picture of what NFPA wants)
3. Can I use 1250gpm pump for this arrangement (max. acc to NFPA 13) of 4 standpipes or I have to add 500gpm (for ordinary hazard, partially sprinklered buildings) to this? Wont 1750 gpm be too big for this scale of building?
3. Using 1250 gpm pump on the underground water tank, I plan on taking 8in main header/supply pipe and extract 6in standpipes from the main on required locations. Is it fine? If I have to use 1750gpm, how much should I increase the pipe sizes?
4. Building total elevation is approx. 150ft. Hence using 1250GPM and setting 120psi at the top most 2 1/2" valve of the remotest riser and using 500gpm for that riser to calculate friction losses plus the friction loss in the 8in main pipe, I get a required pump head of approx. 460'. Is this approach OK?
5. Using 460' pump head, I will have to install a pressure regulator on sprinkler pipe take off at only 1 floor to reduce pressure to lesser than 175 psi in the sprinkler system. But, if I set 100 psi instead of 120 psi at the top, I wont even have to use this regulator, but I used 120 psi to be on safer side. What do you suggest?
6. Lastly, 100 psi min. requirement is at the valve or end of hose pipe (at nozzle)? As I read somewhere, a 150ft hose pipe also induces considerable pressure loss should it be considered while doing pump head calculations?
Thanks in advance for all the help you people can give.