Is it allowable to place the diagonal brace of a Special Concentrically Braced Frame (SCBF) in the weak axis of a wide flange column? I have a column which is in the corner of the structure and I want to be a brace in both directions. Can I do this or do I need to move the brace in the weak direction of the column to another location?
 
Replies continue below

Recommended for you

Yes, what you propose is acceptable.
But be aware that SCBF connection needs to have a strength sufficient to resist the expected ful yield force (Ry*Fy*Ag) in the brace for tension and the expected buckling load (Fcrit*Ag) in compression. This can result in rather substantial connections compared to the brace member. It is advisable to consider using a "system not specifically designed for seismic resisitance" (R=3) if permited by the code, even AISC advises this to avoid the Seismic Provisions (selecting SCBF automatically requires the Seismic Provisions details reguardless of Seismic Design Catagory.
 