jimmy2times
Electrical
- Jun 26, 2007
- 138
We have a motor starter on ship that has the overload wired before the contactor in the power circuit. This doesn't seem right and follows the natural convention ive followed over years to put overload after contactor as per OEM circuit arrangement for coordinated components. Im from IEC part of world so familiar with type 2 coordination iaw IEC 60947-4-2
It then got me thinking what is the issue if overload preceeds contactor in the circuit. Is it just natural convention that has developed over years or it is because this is how the components are tested and that is the arrangement in which they are validated for e.g type 2 coordination.
I was thinking through short circuit and overload conditions and how each component in the string would react and i could not see an issue with overload preceeding contactor.
I was thinking maybe contactor welding and requirement for minimum impedance in circuit for clearance of fuse. But that was clutching at straws.
This is circa 3kw low voltage rating rather than bigger motors.
Would be grateful of reasoning if other than the natural convention that was always adopted.
Thanks.
It then got me thinking what is the issue if overload preceeds contactor in the circuit. Is it just natural convention that has developed over years or it is because this is how the components are tested and that is the arrangement in which they are validated for e.g type 2 coordination.
I was thinking through short circuit and overload conditions and how each component in the string would react and i could not see an issue with overload preceeding contactor.
I was thinking maybe contactor welding and requirement for minimum impedance in circuit for clearance of fuse. But that was clutching at straws.
This is circa 3kw low voltage rating rather than bigger motors.
Would be grateful of reasoning if other than the natural convention that was always adopted.
Thanks.