What is your favorite detail for a long span joist parallel to an exterior wall? A few options:
1. Space the joist off the wall, say 6' and use a ledger angle to pick up the metal deck. The angle will support the deck for dead loads. The deck top flutes are cut so that it can be manipulated and welded to the angle.
2. Same as #1 but direct the contractor to install the angle in segments to match the joist camber profile.
3. Place the end joist close to the wall, say 8" off the wall and cantilever the deck. Provide an angle with slotted holes. In this case the angle transfers out of plane lateral load and in plane lateral load.
For #1 and #2 the deflection of the joist will warp the deck and you might have problems with installation. Also you may need to install a truss system or some sort of additional out of plane bracing for the exterior wall.
For #3, you take care of deflection, but you don't have much room if you wanted to install an in-plane truss to help transfer out of plane loads from the wall. You need to rely on tension/compression of the deck.
Thanks!
EIT
1. Space the joist off the wall, say 6' and use a ledger angle to pick up the metal deck. The angle will support the deck for dead loads. The deck top flutes are cut so that it can be manipulated and welded to the angle.
2. Same as #1 but direct the contractor to install the angle in segments to match the joist camber profile.
3. Place the end joist close to the wall, say 8" off the wall and cantilever the deck. Provide an angle with slotted holes. In this case the angle transfers out of plane lateral load and in plane lateral load.
For #1 and #2 the deflection of the joist will warp the deck and you might have problems with installation. Also you may need to install a truss system or some sort of additional out of plane bracing for the exterior wall.
For #3, you take care of deflection, but you don't have much room if you wanted to install an in-plane truss to help transfer out of plane loads from the wall. You need to rely on tension/compression of the deck.
Thanks!
EIT