I am looking for information on a slab made up of 3" stone conc fill over deck type nkx-16-16. Has anyone see load tables, geometry, etc, for that type of slab?
 
Replies continue below

Recommended for you

The H. H. Robertson Company put out a steel deck, 24" widths, that were described and rated in an old ICBO report, #1388, and dated November, 1980.

The structural properties are listed on page 22 , Table -1, and the load ratings on Page 17, Table D-3. Page 27 has a sketch of the geometry.

I can scan those three pages and post them here for you later today.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
thank you. yes, i am interested, pls post the info
 
As for the load tables, of which there are several, it shows for a 2.5" and 3.25" infill for Normal and Lightweight concrete.

I'll post the three pages I have and you will have to choose:

Page 15: 2.5" Normal Weight

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
 http://files.engineering.com/getfile.aspx?folder=8871a0a7-d112-4da6-b020-5c6b8f4f73fb&file=ICBO_Report_1388_Page_15.jpg
Page 17: 3.25" Lightweight

That's it for the applicable load tables.

I also have tables with allowable diaphragm shears here too if you need them. Let me know. I'll have to check back later as I have an appt.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
 http://files.engineering.com/getfile.aspx?folder=6c13edb9-233d-4308-b8e8-d607ee88954e&file=ICBO_Report_1388_Page_17.jpg