Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Looking for lb/sq ft rating

Status
Not open for further replies.

JTDunn1

Industrial
Aug 25, 2009
2
I have a 12' x 12' loft made of 3/4" thick plywood. There are 2" x 4" studs spaced with a center to center distance of 16". I need to put up warning signs for maximum load per sq foot on this loft but cannot remember or find the proper calculation. Thanks.
 
Replies continue below

Recommended for you

Yes. I agree with boo1. We would have to know the joist size, spacing, and species to help you with that, assuming that the joists frame directly to the 2X4 bearing walls with no beams in the 2X4 walls.

Addidionally, what the walls frame to below would have to be checked as this could also limit the capacity of the loft in the bigger picture.

Mike McCann
MMC Engineering
 
Assuming the 2x4 studs are placed vertically around the perimeter from your plywood floor upward, they have little to do with anything. As Boo1 and Mike said...we need more info.

What supports the 3/4" plywood floor? Do you have truss joists? Lumber joists? What is the spacing? What is the span?
 
If you need to put up warning signs about the loft capacity, you should go hire a structural engineer to do this for you if you can't.

 
I get the uneasy feeling that the OP meant 2x4 joists when he said 2x4 studs.
 
If the joists are 2x4 then consider the load rating as: "no loading allowed/not for storage"
 
Status
Not open for further replies.

Part and Inventory Search