ahmedhelmy87
Mining
- May 29, 2018
- 1
Welcome dears,
I am working at alumina refinery plant and I have had an issue in level transmitter of lubrication tank for 3 years.we have two problems with oil in the tank. first one, Oil viscosity is very high. it looks like grease. the second problem, there is too much foam accumulates on the top of oil surface.
Specification:
tank height is 1.4 m, oil specific gravity is 0.97, tank is atmospheric pressure.
Actions:
During commission, pressure transmitters was installed at the bottom of the tank but it wasn't accurate because pressure head is low. it is about 1300mmwater (13KPA) when tank is fully. so we moved to ultrasound level transmitters, but it is also failed because of foam issue, foam reaches at blocking distance below transducer and started to confuse transmitter then reading is gone or flactuated.
we have recently got some recommendations from Emerson to install GWR 5301, we installed and it was ok for only one week then reading started to go down gradually till reading became zero. when i took sensor out for inspection, i found probe was covered by this oil (grease). once i cleaned and reinstalled again, reading was ok for only a week then problem came again.
i am looking for a stable solution that can be worked with this conditions? Any suggestions?
I am working at alumina refinery plant and I have had an issue in level transmitter of lubrication tank for 3 years.we have two problems with oil in the tank. first one, Oil viscosity is very high. it looks like grease. the second problem, there is too much foam accumulates on the top of oil surface.
Specification:
tank height is 1.4 m, oil specific gravity is 0.97, tank is atmospheric pressure.
Actions:
During commission, pressure transmitters was installed at the bottom of the tank but it wasn't accurate because pressure head is low. it is about 1300mmwater (13KPA) when tank is fully. so we moved to ultrasound level transmitters, but it is also failed because of foam issue, foam reaches at blocking distance below transducer and started to confuse transmitter then reading is gone or flactuated.
we have recently got some recommendations from Emerson to install GWR 5301, we installed and it was ok for only one week then reading started to go down gradually till reading became zero. when i took sensor out for inspection, i found probe was covered by this oil (grease). once i cleaned and reinstalled again, reading was ok for only a week then problem came again.
i am looking for a stable solution that can be worked with this conditions? Any suggestions?