thermionic1
Electrical
- Nov 30, 2018
- 323
I was recently doing a relay upgrade on an unusual station that had 2 lines, 2 buses, but only one set of VT's. We were told by system protection that there was a concern about LOP mis-operations on the line that was staying in service. A protection outage was requested to pull all of the trips from the other line, being radial fed with current diff in place as well as Z2 timer at remote end disabled.
I didn't get a straight answer from the protection engineer, and he transferred jobs in the middle of the project, so I pull the trips on my end. No LOP targets, no LOP SER, nothing. A few weeks later at a different station with 3 lines and a single set of VT's we had a similar but different challenge which was to replace the VT secondary terminal blocks in the house. We did the X winding (primary relays) then the Y winding (secondary). Still had an outage request to have trips off during the cutover. Same relays in play and still no LOP alarms, targets or SER records.
Is this a real issue or was the outgoing protection engineer misguided? He emphasized the 311C as being troublesome. IIRC, the 311C and 311L are identical other than the diff board, or at least that's what SEL said years ago when it came out.
Has anyone else experienced mis operations due to loss of a VT signal?
I didn't get a straight answer from the protection engineer, and he transferred jobs in the middle of the project, so I pull the trips on my end. No LOP targets, no LOP SER, nothing. A few weeks later at a different station with 3 lines and a single set of VT's we had a similar but different challenge which was to replace the VT secondary terminal blocks in the house. We did the X winding (primary relays) then the Y winding (secondary). Still had an outage request to have trips off during the cutover. Same relays in play and still no LOP alarms, targets or SER records.
Is this a real issue or was the outgoing protection engineer misguided? He emphasized the 311C as being troublesome. IIRC, the 311C and 311L are identical other than the diff board, or at least that's what SEL said years ago when it came out.
Has anyone else experienced mis operations due to loss of a VT signal?