Looking for advice and recommendations on properly allocating KW and KVAR losses across multiple transformers sharing a transmission line and then further allocate each transformer line loss share to its related resources/feeders under each transformer.
Assumptions -
1. Three transformers connect to common T-line. Each transformer has both PV and BESS resource feeders on low side.
A. PV operates +/-.95 PF, generation only.
B. BESS can operate +/-.5 PF, discharge or charge.
2. Revenue Meters are placed at each key point to capture real-time Current, KVA, PF, KW and KVAR to perform loss calculations and allocations as needed. i.e Meters at each resource feeder bus connection, at each high-side transformer bus connection, and at far end of line (point of delivery).
3. Resources -
4. Losses -
5. Resources are to share associated accumulated losses. Exception if net flow through transformer to line is + (Delivered to load), BESS is fully charging and will be assigned all losses.
Questions -
1. What is best method to allocate both KW and KVAR line losses to each Transformer, using any combination of Currents, KVA, PF, KW and KVAR from available meters?
2. Each transformer's line loss is determine by solution to above Q1. Then line loss result is combined with transformer losses, with result to be total losses to be allocated to Resources. What is best method to allocate losses both KW and KVAR total losses to each Resource, using any combination of Currents, KVA, PF, KW and KVAR from available meters?
Assumptions -
1. Three transformers connect to common T-line. Each transformer has both PV and BESS resource feeders on low side.
A. PV operates +/-.95 PF, generation only.
B. BESS can operate +/-.5 PF, discharge or charge.
2. Revenue Meters are placed at each key point to capture real-time Current, KVA, PF, KW and KVAR to perform loss calculations and allocations as needed. i.e Meters at each resource feeder bus connection, at each high-side transformer bus connection, and at far end of line (point of delivery).
3. Resources -
A. Any PV may be generating or idle depending on maintenance or night time.
B. Any BESS may be discharging or charging KW and/or sourcing +/- VARs.
C. With active VARs requirements, allocation of VAR losses for all resources to be applied through separate allocation calc than KW loss allocation.4. Losses -
A. KW and KVAR line losses are determined by the difference of the Line meter and the summed High-side meters.
B. Each transformer KW and KVAR losses are determined by the difference of its High-side meter and its summed Low-side resource meters.5. Resources are to share associated accumulated losses. Exception if net flow through transformer to line is + (Delivered to load), BESS is fully charging and will be assigned all losses.
Questions -
1. What is best method to allocate both KW and KVAR line losses to each Transformer, using any combination of Currents, KVA, PF, KW and KVAR from available meters?
2. Each transformer's line loss is determine by solution to above Q1. Then line loss result is combined with transformer losses, with result to be total losses to be allocated to Resources. What is best method to allocate losses both KW and KVAR total losses to each Resource, using any combination of Currents, KVA, PF, KW and KVAR from available meters?