HI THERE, OUR BEST REGARD;
FIRST, SORRY FOR OUR BAD ENGLISH, WE ARE A TROUBLE WITH OUR DECS-200. WE HAVE A 4.6 MW GENERATOR, WHEN WE GIVE THE STOP COMMAND, 3 SECONDS LATER OPENS THE GENERATOR'S SWITCH THEN APPEAR ON SCREEN VOLTAGE MATCHING,OF COURSE, THE GENERATOR VOLTAGE DECREASE AND 2 SECONDS LATER APPEAR "LOST VOLTAGE SENSING" ALARM AND TRIP 86E TROUGH RELAY 3 BECAUSE WE SET SO. OUR QUESTION IS WHY APPEAR THAT ALARM WHILE GENERATOR IS STOPPING, AS SOON AS STOP, WE RESET AND EVERYTHING TURN INTO NORMAL, IN NORMAL OPERATION THE DECS-200 WORKS ON PF CONTROL AND DOESNT TURN TO FCR IF LOST OF SENSIG OCURRS. PLEASE HELP US
FIRST, SORRY FOR OUR BAD ENGLISH, WE ARE A TROUBLE WITH OUR DECS-200. WE HAVE A 4.6 MW GENERATOR, WHEN WE GIVE THE STOP COMMAND, 3 SECONDS LATER OPENS THE GENERATOR'S SWITCH THEN APPEAR ON SCREEN VOLTAGE MATCHING,OF COURSE, THE GENERATOR VOLTAGE DECREASE AND 2 SECONDS LATER APPEAR "LOST VOLTAGE SENSING" ALARM AND TRIP 86E TROUGH RELAY 3 BECAUSE WE SET SO. OUR QUESTION IS WHY APPEAR THAT ALARM WHILE GENERATOR IS STOPPING, AS SOON AS STOP, WE RESET AND EVERYTHING TURN INTO NORMAL, IN NORMAL OPERATION THE DECS-200 WORKS ON PF CONTROL AND DOESNT TURN TO FCR IF LOST OF SENSIG OCURRS. PLEASE HELP US