nicholi
Structural
- May 25, 2002
- 24
I have received the test results for a seven day break at 11.3 MPa. The design strength is 25 MPa. Based on the seven day break being 65% of max strength, the 28 day break should be 17.4 MPa.
The low concrete is for a canopy pad (with pedestal above) for a gas retail site.
I have proven theoretically that there is sufficient concrete strength to accept the canopy loads from above acting in compression on the pad below.
However, I don't feel satisfied and think I might have overlooked something and still want to tell the contractor to remove the concrete. (I know what the code says in terms of low strength concrete and acceptance.)
Any comments, opinions, ideas. Thanks in advance for the feedback.
I have researched the code stuff and know what their an
The low concrete is for a canopy pad (with pedestal above) for a gas retail site.
I have proven theoretically that there is sufficient concrete strength to accept the canopy loads from above acting in compression on the pad below.
However, I don't feel satisfied and think I might have overlooked something and still want to tell the contractor to remove the concrete. (I know what the code says in terms of low strength concrete and acceptance.)
Any comments, opinions, ideas. Thanks in advance for the feedback.