msucog
Civil/Environmental
- Feb 7, 2007
- 1,044
had some low grout prism strengths show up on a job. the prisms were made from the first set of onsite mixed grout. we checked the proportions and it looks like they were mixing grout with sand:grout of 2.7:1 (type I cement). this falls within ASTM's table of proportions for grout (2.25-3 ratio) if i'm correct...HOWEVER the grout is spec'd out at 3000psi not 2000psi. i'm pretty sure this is the culprit. the strength came up at ~2500psi. does anyone have a cubic foot measurement of what the sand:cement ratio should approximately be for 3000+psi grout. i'm estimating 1.5-1.7:1 sand:cement ratio to get up above 3000psi but this is very ballpark. i'm not proposing to give the contractor the correct proportioning but i'm more curious than anything so that i can have a heads up for next time this comes up.
any help would be appreciated...