NoHoCa
Mechanical
- Jun 19, 2006
- 32
I'm checking head losses on an air header that delivers about 1400 cfm at 10.5 psig and 200F (average in pipe) from a blower. The main header is 20" steel pipe, which I think is plenty oversized for minimal friction losses. So I expect the losses to be perhaps only a fraction of an inch. The Reynolds number is less than 100, so apparently quite laminar.
I've been told that the "Friction Loss in Standard Duct" table (MERM, Lindeburg, Fans & Duct chapter) is the way to go. But I'm suspicious because it's intended for building ducts, not pressurized process piping.
So I tried the Darcy equation. But the problem is that at very low Reynolds numbers, the friction factor f=64/Re. Instead of a fractional factor (and low head loss), I get an "f" of about 1 (with Re=63). That translates into a head loss of about 250 feet over 76' of 20" piping. Which is wrong because we know the existing system should only drop a few inches in air pressure, if that.
What am I missing here? Is the Darcy eqn really worthless for laminar flow? Did I miss a conversion (don't think so, my units checked)? Thanks for any advice on Darcy versus the old Duct table...
I've been told that the "Friction Loss in Standard Duct" table (MERM, Lindeburg, Fans & Duct chapter) is the way to go. But I'm suspicious because it's intended for building ducts, not pressurized process piping.
So I tried the Darcy equation. But the problem is that at very low Reynolds numbers, the friction factor f=64/Re. Instead of a fractional factor (and low head loss), I get an "f" of about 1 (with Re=63). That translates into a head loss of about 250 feet over 76' of 20" piping. Which is wrong because we know the existing system should only drop a few inches in air pressure, if that.
What am I missing here? Is the Darcy eqn really worthless for laminar flow? Did I miss a conversion (don't think so, my units checked)? Thanks for any advice on Darcy versus the old Duct table...