rockman7892
Electrical
- Apr 7, 2008
- 1,156
Has anyone come across or have experience with LRG applied on a 480V system? I'm looking at a proposed project application that is calling for an 400/5 LRG applied on the neutral of (2) 4MVA 480V secondary transformers feeing a M-T-M 480V switchgear lineup.
I've always seen High Resistance Ground (HRG) systems applied at 480V level to allow continuous operation on ground fault and always understood LRG systems to be limited to MV systems? I believe I saw somewhere once that with an LRG applied on a 480V system, that under ground fault conditions most of the system voltage would drop across the resistor and may not provide enough voltage to drive ground fault to levels that can be selected by breaker trip units?
I've always seen High Resistance Ground (HRG) systems applied at 480V level to allow continuous operation on ground fault and always understood LRG systems to be limited to MV systems? I believe I saw somewhere once that with an LRG applied on a 480V system, that under ground fault conditions most of the system voltage would drop across the resistor and may not provide enough voltage to drive ground fault to levels that can be selected by breaker trip units?