Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Low risk

Status
Not open for further replies.

facetoface

Electrical
Apr 23, 2005
50
What is the best to do of the energization of power transformer (11/132 KV , 60 MVA) from primary or secondary side at the live busbar.
 
Replies continue below

Recommended for you

Define "best". It all depends on what "best" is in this particular instance.
 
The advatages and disadvatages of energization from both side
 
Hi Facetoface.
Just my opinion, base on few cases was happend at the last mounth.
1. Check first energazing procedure with trafo mnf.
Read this post.
thread238-218517
2. Check all fire systems and gas.
2.1 check place of fire services hydrants and water.
2.2 check push button " fire trouble" and check that this operation disconnect all power supplies.
2.3. Put guys from fire service near to this hudrants with your electrical guys.
2.4 please order one or two mobiles of fire service
3. Check "place" of oil in case of trafo fault.
4. Check option of energazing trafo from very weak line, with lowerst level of SC., if trafo mnf. haven't some special requerements and you have option --energize from low side
5. in additional to diff 87T trafo protection and 50/51
add temprorary 50/51/50N/51N settings with minimum time settings on the infeed line.
Just my opinion.
Best Regards.
Slava
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor