Could you review and comment on my design idea?
I have an existing building with hydronic heat that requires about 140-150°F supply temp. I also add some unit heaters that I design for 140°F. Overall that part may have a dT of 25°F (that design is a bit screwed up, and we add perimeter heat - so that dT is not necessarily accurate n real life). Will require ~100 gpm. Boiler setpoint probably will be 90-140°F depending on OAT and valve positions.
The new building addition will get radiant infloor heating. Currently I plan on designing for 120°F and 20°F dT. It seems many of the loops can et by with lower supply temp. Will also require ~100 gpm.
I attached two options. both have in common:
- condensing boilers will get minimum flow via a bypass valve (each boiler has 25 gpm min flow). Flowmeter will modulate bypass valve to either provide 25 or 50 gpm depending on how many boilers are on.
- they will operate in parallel whenever possible for better efficiency (turndown 1:20) and have each an isolation valve.
- objective is low return temp for better efficiency and also reliability and less complexity
- radiant floor shall be protected from getting more than 150°F to prevent concrete cracking. Under normal operation this would not happen, but have to account for someone setting something wrong or other issues forcing the boiler to provide 180°F etc.
- this needs to work when radiant has no load, or when the high-temp system has no load, or anything in between.
- all zone valves will be 2-way.
- For radiant floor it doesn't matter if the supply temp drops or rises for an hour. If I only get 110 instead of 120Ç° for a while, it isn't really important.
Everything will be fed by a new boiler plant (2 boilers).
Option 1 creates a separate loop with pumps for the radiant heating. Advantage is it could lower return temp more. disadvantage is it has 2 more pumps and at any given time I need radiant heating, 2 pumps need to operate. It also could get too little hot water (only bypass flow) when there is no flow through the high-temp system.
Option 2 creates a scenario where when boiler temp is low, the radiant loop gets straight boiler water. As the temp rises, the 3-way valve will blend boiler return water in to lower water temp to radiant floor. I may adjust control system to keep it warm (maybe 130°F, or also could set it lower, or make that dependent on OAT...). If I'm in a pinch I also could send 140°F water to the radiant floor.
The disadvantage is my boiler return temp will be a bit higher (about 107°F instead of 100°F). Advantage is I need fewer pumps.
Option 2 has the hydraulic property to switch between low and high flow. It could be enhanced to use 3 smaller pumps to improve low-flow efficiency operating just one pump (they will be VFD). One pump is standby, but I think even if 2 pumps fail there could still be decent operation left.
Maybe in theory Option 1 could have more efficient boiler operation, but Option 2 seems to have better pump efficiency. Preliminary pump sizing showed me either way pumps would be 3 hp size (even different models)... but when operating in parallel at design flow two pumps in parallel use less than one pump (per Grundfos sizing tool)
Obviously in real operation at medium load many valves will be throttled, dT should be larger and overall return temp lower.
Option 3 resolves the problem with higher boiler return temp. but hydraulically it may be more challenging as it switches between high flow - lower dP and low flow - higher dP. But my 3-pump idea may help. Option 3 basically switches the radiant flow to be in series to the high-temp system if needed. If for some reason there is no load on high-temp system, I would not have colder water to blend in and added a potential circulation pump (this is only for when boiler goes rogue and provides too hot water). not sure this pump really help. I could accomplish radiant overheating protection by monitoring radiant return temp and throttling the radiant valves. but this could give me a very high dT system.
For option 2 and 3 it seems I need a checkvalve.
I like to know if you have suggestions to improvements or opinions on either scenario. My mechanics like option 2 better for fewer parts and the possibility of three pumps. ( I realize I could have three pumps in option 1 as well, but 6 pumps in total seems unrealistic for space and budget reasons)
I have an existing building with hydronic heat that requires about 140-150°F supply temp. I also add some unit heaters that I design for 140°F. Overall that part may have a dT of 25°F (that design is a bit screwed up, and we add perimeter heat - so that dT is not necessarily accurate n real life). Will require ~100 gpm. Boiler setpoint probably will be 90-140°F depending on OAT and valve positions.
The new building addition will get radiant infloor heating. Currently I plan on designing for 120°F and 20°F dT. It seems many of the loops can et by with lower supply temp. Will also require ~100 gpm.
I attached two options. both have in common:
- condensing boilers will get minimum flow via a bypass valve (each boiler has 25 gpm min flow). Flowmeter will modulate bypass valve to either provide 25 or 50 gpm depending on how many boilers are on.
- they will operate in parallel whenever possible for better efficiency (turndown 1:20) and have each an isolation valve.
- objective is low return temp for better efficiency and also reliability and less complexity
- radiant floor shall be protected from getting more than 150°F to prevent concrete cracking. Under normal operation this would not happen, but have to account for someone setting something wrong or other issues forcing the boiler to provide 180°F etc.
- this needs to work when radiant has no load, or when the high-temp system has no load, or anything in between.
- all zone valves will be 2-way.
- For radiant floor it doesn't matter if the supply temp drops or rises for an hour. If I only get 110 instead of 120Ç° for a while, it isn't really important.
Everything will be fed by a new boiler plant (2 boilers).
Option 1 creates a separate loop with pumps for the radiant heating. Advantage is it could lower return temp more. disadvantage is it has 2 more pumps and at any given time I need radiant heating, 2 pumps need to operate. It also could get too little hot water (only bypass flow) when there is no flow through the high-temp system.
Option 2 creates a scenario where when boiler temp is low, the radiant loop gets straight boiler water. As the temp rises, the 3-way valve will blend boiler return water in to lower water temp to radiant floor. I may adjust control system to keep it warm (maybe 130°F, or also could set it lower, or make that dependent on OAT...). If I'm in a pinch I also could send 140°F water to the radiant floor.
The disadvantage is my boiler return temp will be a bit higher (about 107°F instead of 100°F). Advantage is I need fewer pumps.
Option 2 has the hydraulic property to switch between low and high flow. It could be enhanced to use 3 smaller pumps to improve low-flow efficiency operating just one pump (they will be VFD). One pump is standby, but I think even if 2 pumps fail there could still be decent operation left.
Maybe in theory Option 1 could have more efficient boiler operation, but Option 2 seems to have better pump efficiency. Preliminary pump sizing showed me either way pumps would be 3 hp size (even different models)... but when operating in parallel at design flow two pumps in parallel use less than one pump (per Grundfos sizing tool)
Obviously in real operation at medium load many valves will be throttled, dT should be larger and overall return temp lower.
Option 3 resolves the problem with higher boiler return temp. but hydraulically it may be more challenging as it switches between high flow - lower dP and low flow - higher dP. But my 3-pump idea may help. Option 3 basically switches the radiant flow to be in series to the high-temp system if needed. If for some reason there is no load on high-temp system, I would not have colder water to blend in and added a potential circulation pump (this is only for when boiler goes rogue and provides too hot water). not sure this pump really help. I could accomplish radiant overheating protection by monitoring radiant return temp and throttling the radiant valves. but this could give me a very high dT system.
For option 2 and 3 it seems I need a checkvalve.
I like to know if you have suggestions to improvements or opinions on either scenario. My mechanics like option 2 better for fewer parts and the possibility of three pumps. ( I realize I could have three pumps in option 1 as well, but 6 pumps in total seems unrealistic for space and budget reasons)