power2020

Electrical
Aug 18, 2005
127
0
0
AE
Dear Folks,
Pl. clarify regarding breaking current selection of LV ACB, if L-G fault current is more than 3-ph bolted current , which current needs to be considered for LV ACB breaking capacity? I read somewhere that we need to consider 3-ph bolted fault current to select LV ACB breaking capacity.

Advanced thanks..
 
Replies continue below

Recommended for you

Since each pole of the CB has to interrupt the current, it would not matter whether it was 3 ph or 1 ph current. I would go with the highest current that needs to be interrupted to select a CB.
 
Thank you wbd for your response. Is there any co-relation between LV ACB 3-pole breaking current and 1-pole breaking current? or both are same?
 