In our facility, we have a few 3-phase, 5 & 10 KVA and a few 1-phase, 3 & 5 KVA battery based UPS, many LED lights along with lathes, drilling machines, boring machines, milling machines electric cranes etc., which all have 3-phase motors. I did a voltage and current waveform check today as below.
Voltage THD - Less than 3%
Current THD - Over 20%
I found switching off the UPS one by one helped reduce the current THD to less than 5% thus confirming they are the culprits.
1. Is this high current THD normal when the voltage THD is so low?
2. Is such high current THD detrimental to my facility?
3. Do I need any passive or active filters or chokes at the supply side (front end) of UPS for harmonics mitigation?
4. If yes, should they be individual filters/chokes for each UPS or one big filter/choke at the incomer mains?
Thanks for your suggestions.
Muthu
Voltage THD - Less than 3%
Current THD - Over 20%
I found switching off the UPS one by one helped reduce the current THD to less than 5% thus confirming they are the culprits.
1. Is this high current THD normal when the voltage THD is so low?
2. Is such high current THD detrimental to my facility?
3. Do I need any passive or active filters or chokes at the supply side (front end) of UPS for harmonics mitigation?
4. If yes, should they be individual filters/chokes for each UPS or one big filter/choke at the incomer mains?
Thanks for your suggestions.
Muthu