NickVil
Petroleum
- Feb 3, 2003
- 22
Hi,
We have some flange connections within the LPG Storage bunded areas. This is to, in case of leaks the LPG will stay inside the bund. In the event of fire in such a bund, these flanges would be vulnerable to opening, and provide additional flammable material to the fire.
However some people have observed as current best practice as having no flanges on the bottom of LPG spheres, with minimal in-bund piping, and where present being fully welded with the remote operated isolation valve welded on the sphere side and located outside of the bund.
Is it recommendable to move such connections and piping outside of the bund? I think doing that, in case a leak the LPG will go to some other place instead of the bunded area.
Is there some standard that recommends the position of such valves?
Regards
We have some flange connections within the LPG Storage bunded areas. This is to, in case of leaks the LPG will stay inside the bund. In the event of fire in such a bund, these flanges would be vulnerable to opening, and provide additional flammable material to the fire.
However some people have observed as current best practice as having no flanges on the bottom of LPG spheres, with minimal in-bund piping, and where present being fully welded with the remote operated isolation valve welded on the sphere side and located outside of the bund.
Is it recommendable to move such connections and piping outside of the bund? I think doing that, in case a leak the LPG will go to some other place instead of the bunded area.
Is there some standard that recommends the position of such valves?
Regards