cherryg
Electrical
- Jul 6, 2003
- 48
This question is specific to a MCC Incomer where ABB MCCB is being used rather than an ACB.
The MCCB short ckt interruption capcity is 70kA at 380V. But its short time withstand rating is only 7.3kA at 1 sec.
Now the prospective short circuit current at the MCC bus is 62kA.
If the Manin Incomer fails to trip on a MCC bus fault, the Upstream Switchgear breaker wil trip at 180 to 220 millisec.
But calculating the I^2 t, it appears that the MCCB is not adequately sized for the short time withstand.
Please correct me if I am wrong, but the short time withstand value here is important only if the breaker itself fails to trip.
Please discuss.
The MCCB short ckt interruption capcity is 70kA at 380V. But its short time withstand rating is only 7.3kA at 1 sec.
Now the prospective short circuit current at the MCC bus is 62kA.
If the Manin Incomer fails to trip on a MCC bus fault, the Upstream Switchgear breaker wil trip at 180 to 220 millisec.
But calculating the I^2 t, it appears that the MCCB is not adequately sized for the short time withstand.
Please correct me if I am wrong, but the short time withstand value here is important only if the breaker itself fails to trip.
Please discuss.