Hello!
I'm trying to coordinate ground fault protections for several low voltage motors (2, 5 and 11 kW) that are protected by a C441 Motor Insight (Eaton). About the pickup current, I'm considering 3% of Full Load Current of the motor but for the instantaneous region I'm having trouble as the delay settings vary from 1-60 seconds and the upstream protection has an earth fault time delay of 300 ms (Incoming of the Motor Control Center - NGH800 Eaton), which is the maximum setting.
What I'm doing wrong? I'm considering both protections directly from ETAP's library and re-checked those delay ranges from both of their catalogues.
I'm trying to coordinate ground fault protections for several low voltage motors (2, 5 and 11 kW) that are protected by a C441 Motor Insight (Eaton). About the pickup current, I'm considering 3% of Full Load Current of the motor but for the instantaneous region I'm having trouble as the delay settings vary from 1-60 seconds and the upstream protection has an earth fault time delay of 300 ms (Incoming of the Motor Control Center - NGH800 Eaton), which is the maximum setting.
What I'm doing wrong? I'm considering both protections directly from ETAP's library and re-checked those delay ranges from both of their catalogues.