jps1
Electrical
- Mar 1, 2011
- 10
On our Transformer LV side I have SC currents of up to 50kA. The transformers are typically 1MVA 3.3kv to .42kv. They were manufactured in the 1950 to early 1960 and have a %Z of 1.92.
The secondary tie CB are normally operated open. When close, the SC level goes up to approx. 100kA.
My question is this, base on the NEC or IEEE standard, is there a requirement to have the LV switchgear braced for 100kA? The tie CB is rarely closed and it done only when one transformer is taken out for maintenence.
Regards
The secondary tie CB are normally operated open. When close, the SC level goes up to approx. 100kA.
My question is this, base on the NEC or IEEE standard, is there a requirement to have the LV switchgear braced for 100kA? The tie CB is rarely closed and it done only when one transformer is taken out for maintenence.