1
- #1
StructuralGuy68
Structural
- Jun 24, 2022
- 2
Hi all,
I am designing a renovation to my house (built in '69) by removing a load bearing wall (~25.5' span) on the main level of my house. My house is a 1 story rancher with a basement. I used the attic (uninhabitable) loading of 20psf LL and 10psf DL. I am recessing an LVL into the ceiling with rafter ties on joist hangers and carrying the load down to the basement using columns that will be incorporated into walls on each end (one perpendicular an one in-line with the LVL).
The question is when reaching the basement, do I need to install footers? I have original blueprints of my house showing a 4" unreinforced slab. I drilled a test 1/16" hole thru the slab to confirm and it is 4" thick. Using ACI 318-14 section 14.5.5.1 (2.667*λ*sqrt(f'c*b.o*h)) for two way shear I am only getting a 0.71 utilization ratio using the plain concrete 4" slab vs the factored loading that the columns will never see (only way to apply the 20psf LL storage would be to climb over the HVAC in the attic). Cutting into the slab and installing footers is complicated based on one end being basically next to/under the stair stringer (roughly mid height on stairs) to the basement and the other end being next to a masonry laundry shoot which would have to be undermined by the footer. So if possible I would like to bear my columns right on the slab but I would be relying solely on the slab. Thoughts? Things I am not considering?
I am designing a renovation to my house (built in '69) by removing a load bearing wall (~25.5' span) on the main level of my house. My house is a 1 story rancher with a basement. I used the attic (uninhabitable) loading of 20psf LL and 10psf DL. I am recessing an LVL into the ceiling with rafter ties on joist hangers and carrying the load down to the basement using columns that will be incorporated into walls on each end (one perpendicular an one in-line with the LVL).
The question is when reaching the basement, do I need to install footers? I have original blueprints of my house showing a 4" unreinforced slab. I drilled a test 1/16" hole thru the slab to confirm and it is 4" thick. Using ACI 318-14 section 14.5.5.1 (2.667*λ*sqrt(f'c*b.o*h)) for two way shear I am only getting a 0.71 utilization ratio using the plain concrete 4" slab vs the factored loading that the columns will never see (only way to apply the 20psf LL storage would be to climb over the HVAC in the attic). Cutting into the slab and installing footers is complicated based on one end being basically next to/under the stair stringer (roughly mid height on stairs) to the basement and the other end being next to a masonry laundry shoot which would have to be undermined by the footer. So if possible I would like to bear my columns right on the slab but I would be relying solely on the slab. Thoughts? Things I am not considering?