XR250
Structural
- Jan 30, 2013
- 5,293
Was in a crawlspace today of a 3 story, wood framed condo. Was there investigating continued complaints of sheetrock cracks. Based on my laser measurements, pier settlement seems to be the biggest offender. However, I also observed many instances of the 3-ply, 18" LVL beams in the crawlspace showing signs of crushing over their SYP wood blocks (see attached). I measured about 1/4" of crushing with a computed existing load reaction of about 7k or 200 PSI perp. to grain. The SYP appears unfazed by the load. WTF? I though the LVL design values were about 750 psi for perp. to grain loading.
The LVL brand is "Weldwood" which appears to have been bought out years ago. My guess is no help from the new owner.
The building is 10 years old and pretty consistently lightly loaded with retirees (trussed roof clear spans the crawlspace). As such, I doubt the load changes much. Do you think the crushing has done all it is going to do?
The LVL brand is "Weldwood" which appears to have been bought out years ago. My guess is no help from the new owner.
The building is 10 years old and pretty consistently lightly loaded with retirees (trussed roof clear spans the crawlspace). As such, I doubt the load changes much. Do you think the crushing has done all it is going to do?