mfstructural
Structural
- Feb 1, 2009
- 230
I'm designing an LVL to support floor joists and remove a bearing wall. There are several openings they want to make and have the ceiling open. the contractor wants to install one long LVL (18' long). The opening is 115", then there is a closet which the beam will sit on, and then span the opening over the entrance which is 32 inches. I started a thread yesterday regarding sistering the joists. This post is regarding the LVL. The other post can be found here:
When I run numbers on a s.s. beam for the 115" span they show I need 3 plies of 7.25" LVL (they don't want to go taller than that with LVL since the joists will be 2x8s). By increasing the E to 2.0 and Fb to 2850, I can get the beam to work. The interaction ratio is 1.0 for bending. The deflection is my concern then. Since the beam is not simply supported in reality...it's a 115" span with the second span partially over a closet (bearing for 48") and partially spanning an opening (approximately 32"). Because of this my thought is that the deflection in reality is not really 5wl/384EI, but could be 1wl/185EI because it more resembles a two span beam with one span loaded...I know it's a gray area and judgement, but I'm trying to get a 2 ply beam to work.
The last question is that I called around some lumber yards to just see if they have 2.0E LVLs and what the bending strength is. When I asked bending strength they all said they don't know they just know the E. So many lumber yards have LVLs with 2.0E, but how can you be sure what the Fb is? I got the feeling when I spec out a 2850 how do I know that's what the Fb really is? I know Fb can be 2850, 2900, or 3100 for 2.0E? If I specified Fb = 3100 the 2 ply beam would work for sure.
The last thing is that the attic above has a gable roof so there won't be any load near the two long walls of the residence as there is no head room. For purposes of design, I don't think you'll ever have 40 psf there, especially if they building a knee wall and wall it off.
I included a picture for reference
When I run numbers on a s.s. beam for the 115" span they show I need 3 plies of 7.25" LVL (they don't want to go taller than that with LVL since the joists will be 2x8s). By increasing the E to 2.0 and Fb to 2850, I can get the beam to work. The interaction ratio is 1.0 for bending. The deflection is my concern then. Since the beam is not simply supported in reality...it's a 115" span with the second span partially over a closet (bearing for 48") and partially spanning an opening (approximately 32"). Because of this my thought is that the deflection in reality is not really 5wl/384EI, but could be 1wl/185EI because it more resembles a two span beam with one span loaded...I know it's a gray area and judgement, but I'm trying to get a 2 ply beam to work.
The last question is that I called around some lumber yards to just see if they have 2.0E LVLs and what the bending strength is. When I asked bending strength they all said they don't know they just know the E. So many lumber yards have LVLs with 2.0E, but how can you be sure what the Fb is? I got the feeling when I spec out a 2850 how do I know that's what the Fb really is? I know Fb can be 2850, 2900, or 3100 for 2.0E? If I specified Fb = 3100 the 2 ply beam would work for sure.
The last thing is that the attic above has a gable roof so there won't be any load near the two long walls of the residence as there is no head room. For purposes of design, I don't think you'll ever have 40 psf there, especially if they building a knee wall and wall it off.
I included a picture for reference