Machine Dynamics: H factors

Status
Not open for further replies.

Vegemite

Electrical
Jul 28, 2002
28
In order to calculate the longest fault clearance times permissible in an industrial power system I need 'stored energy constants' or H factors (in seconds) for the turboalternators. All machines are powered by 8,000 rpm steam turbines via gearboxes. These turbines are pass-out or non-condensing types supplying process steam in an aluminium refinery. The turboalternators are 50 Hz and as follows:
-- 1500 rpm, 12 MVA turboalternator
-- 1500 rpm, 20 MVA turboalternator
-- and 3000 rpm, 12 MVA turboalternator.

The H factor values need to include all of the rotating components, that is, steam turbine, gearbox and alternator.

As an alternative to the H factor the moment of inertia, J in kg M², for each component of the drive train and the speed of each component of the drive train together with the alternator's MVA rating would suffice.
 
Replies continue below

Recommended for you

Please ask to the manufacturers of the alternators and the turbines.
 
Hello,

Maybe look at the thread I asked about H values last week. I got a very good answer from Marmite.

Basically you have the MVA and the speed and the H value is equal to 1/2Jw^2/MVA. So you just need J. you can look in the equipment spec's, ask the manufacturer or calculate it using for example J=1/2mr^2 for a disk.

Good luck.
 
Check the thread on : Hydropower Unit Inertia Requirement
 