elmatador
Electrical
- Jun 10, 2009
- 22
Hi Everyone,
We have a main-tie-main configuration for our system. When reverting back to normal service we want to use a closed transition re-transfer so that we don't have stop all the motors in the facility and cause a process upset. Both A and B sources on the M-T-M are fed from a utility source. When carrying out the short circuit study, I noticed that the fault levels are quite substantial when paralleling up the two transformers (which makes sense). It is around 78kA and the gear is only rated for 65kA. Since this re-transfer would only take a couple of cycles, is it recommended to beef up all the switchgear and mcc ratings to Sym. 85kA? The parallel operation will never be used in a Continuous Operation. Please let me know your comments.
Thanks in advance.
We have a main-tie-main configuration for our system. When reverting back to normal service we want to use a closed transition re-transfer so that we don't have stop all the motors in the facility and cause a process upset. Both A and B sources on the M-T-M are fed from a utility source. When carrying out the short circuit study, I noticed that the fault levels are quite substantial when paralleling up the two transformers (which makes sense). It is around 78kA and the gear is only rated for 65kA. Since this re-transfer would only take a couple of cycles, is it recommended to beef up all the switchgear and mcc ratings to Sym. 85kA? The parallel operation will never be used in a Continuous Operation. Please let me know your comments.
Thanks in advance.