I need to do maintenance testing on digital current differential relay. Besides the current diff function the relay is also used for directional OC & EF as well as reverse busbar blocking (RBBB). It serves an 11kV network. The relay was tested to death with commissioning when every single item was tested down to the last LED. I am now wondering what tests are necessary 8 years down the line? My think is as follows:
For the current diff function:
1. test pickup from both ends.
2. test at one point on each of its dual slopes.
OC & EF
1. IDMT - pickup and one point on curve
2. Def time - pickup and timing test
Logics, inputs, outputs and LED's
I think it vital to prove all logics that will result in trips such as the RBBB.
But do I check every I/O and LED? Comments?
Thanks.