What size pipe are you using? This will, of course, affect the "n" you use.

I've typically seen something in the neighborhood of 0.01-0.016 used for 3"-8" pipe; 0.016-0.018 for 10"-12" pipe and 0.019-0.021 used for larger than 12".

Maybe some others can shed more light on this for you in the way of actual sources, of specific values, for varying cases.

H2H
 
The slots only account for 5% of the total area within on linear foot. So the slots will make a slight impact but not alot.
 
I agree with Uni-Bell that the n=0.009 is probably accurate for PVC flowing full. Many suggest using 0.011 because Camp (circa 1950) found that n-values vary with depth. According to his findings the max n/n0 = 1.2. Which 0.009 * 1.2 = 0.011. Whether Camp's study is applicable to smooth pipes is conjectural. I tend to use n = 0.011. For perf. or slotted pipe I might be temped to use n=0.012.
 