Civilchica,
So it took a few days but I wanted to confirm my research with our senior engineer who has been out of the office.
In reading one of the last letters I received from EBMUD (one of the water agencies here in the area), one of the paragraphs after reporting their test results reads as follows:
"The flow and pressure (static and residual) is available at the street main connection. It is recommended that the fire sprinkler designer incorporate allowance for pressure losses through the fire service meter, backflow prevention, and the lateral from the street main to the fire service meter"
EBMUD does not carry out a physical fire flow test, rather they run their computer model and report their results. Like I mentioned before, I have not ran into projects where the available pressure was so low that the pressure loss had to be calculated that close. However, I have run the hand calculations to verify those losses just to be on the safe side.
What I did fail to mention last time was that within WaterNetworks by Boss International, the losses in a stretch of pipe can be entered when defining that pipe. That is losses due to bends, contractions, expansions, entrance and exits, etc can be incorporated into the model by adjusting the loss coefficient of that pipe run. This would be the place within the program where you could account for those orifice losses. However for the size of projects that I have been involved with, the hand calculation has sufficed. I would incorporate those hand calculations into the program if I was modeling a much larger project.
Everyone,
The attachment includes an excerpt from the 2006 IFC which describes the reasoning behind the 20 psi requirement. I have encountered fire department officials that will allow dipping into the 20 psi requirement but like FED3 mentions, that is their safety factor and therefore they have the final say. Now typically this will be a 2 o 3 psi drop below in the 20 psi requirement. In the last project I was involved, the pressure dropped to 11 psi when applying the required demand. This loss was also affected by the topographical features of the site and therefore a pump will be installed to mitigate this problem.
I hope this helps.