Civilchica
Civil/Environmental
- Mar 26, 2010
- 5
I have a project with an existing 12" water main out front, and an existing fire hydrant coming off a 150-foot long 8" dead end main onsite. We are expanding the existing building and the plan checker has asked for calculations proving we have residual pressure of 20psi for a flow of 1500gpm at the existing hydrant. We just did fire flow testing using two hydrants on the 12" main out front. Results are 70psi static, 40psi residual, 32psi pitot, 950gpm flow. I want to just do a quick hand calculation using the energy equation, but I am unsure about one thing. For my velocity at the fire hydrant, do I use the velocity based on the 2.5" hydrant orifice, or based on the 8" pipe. In the past I've used WaterCAD or the water district ran the calculations, and I don't think they factor in the fire hydrant orifice size. But I believe the fire hydrant testing does, so I don't know which to use and it makes a huge difference. Any feedback would be appreciated.