Manual Volume Dampers on Return and Exhaust Ducts

Status
Not open for further replies.

Igc15

Mechanical
Mar 31, 2021
1
It's usual to insert manual volume dampers before a diffuser in all supply ducts branches. Is this also applied for return and exhaust ducts?
 
Replies continue below

Recommended for you

it depends on if there is a need to balance.

For example, if you have a single VAV box serving a single diffuser, you don't need a damper. you only need dampers to balance flows between 2+ diffusers.

You also can have return or exhaust VAV boxes, BTW. Or if you have a single fan exhausting from a single hood, no balancing needed.
 
If you need to balance, and all air systems should be balanced, you need dampers at all outlets/inlets.
 