I have a building that is currently under construction that I am quite miffed about. The building is utilizing some CMU stair shafts as shear walls. We are grouting the walls solid and have give the contractor the option to do low lift grouting or high lift grouting. The contractor selected the use of high lift grouting.

During my last visit to the site, the CMU walls were being constructed and had yet to be grouted. I commented and noted in my field report that since high lift grouting was being utilized that cleanout holes would be at the bottom of the CMU would be required. The contractor complained but I told them the information was clearly on the drawings and they were the ones who selected high lift grouting for their ease.

Fast forward to my field visit today, when grouting of the CMU walls was complete... with not a cleanout hole on the entire project.

I am not sure what to do in this instance. Very angry right now.
 
Replies continue below

Recommended for you

We had a project several years ago that had a CMU issue. They performed an infrared scan with a ThermaCAM T420, and it perfectly showed which cells were grouted. Not sure of cost or who paid.
 
Is it just a matter to prove that it is grouted? I was always understood the requirement for cleanouts as to clean out the mortar droppings from the bottom of the grouted cells to allow for proper bonding of the grout to the concrete wall/grouted lift. The mortar droppings will be in hardened clumps with various voids throughout the base of the lift...... not really a good situation.
 
Then what do you do when you find the inevitable voids? Fun analysis.
Sounds like it's a contractor problem to fix at that stage no? Pressure grouting is a reasonable solution in my mind. One hole at the bottom of each void, one at the top, pressure grout in the bottom until it comes out the top. Rinse and repeat as necessary at each void.

Is this going to be painful, absolutely it is. But such is life sometimes when you don't follow directions.
 
Honestly, I feel like this (having grout clean outs) is standard practice that most experienced contractors should have caught really early on.

I haven't worked on very many masonry projects. But, I did do a couple of remodels of existing older building were we used GPR to determine grouting and reinforcement spacing. No one was really worried about that cost, though I don't know the actual numbers.

At this point, that GPR is (IMO) a good solution for everyone. Or, any form of non-destructive testing.
a) It's probably not all that expensive when compared to other options at this point. There are companies that specialize in this sort of thing and seem to be pretty good (and quick) with their work.
b) It will demonstrate how well they did the grouting. If they did a great job, they are vindicated. But, they still should foot the bill for this cost.
c) The owner (and you the engineer) can rest easier knowing you've really got.

I'm wondering what happens if (or when) voids are detected. Are there less intrusive methods to solve this problem other than busting open the wall wherever you find them. Like making smaller grout holes only where the voids are detected?
 
The bottom of the grouted columns could be cored. If too much debris, cleaned out and dry-packed.
 
Is this a commercial building? Are Special Inspections per IBC Chapter 17 not required? SteelPE, are you performing the Special Inspections? If not, what has the Special Inspector reported for verification of the grout space prior to grouting? Special Inspections, which are really sort of a pain in the neck, are supposed to catch stuff like this.
 
Is it just a matter to prove that it is grouted? I was always understood the requirement for cleanouts as to clean out the mortar droppings from the bottom of the grouted cells to allow for proper bonding of the grout to the concrete wall/grouted lift. The mortar droppings will be in hardened clumps with various voids throughout the base of the lift...... not really a good situation.
Have them cut on the face on a number of the cells at the bottom of the wall to prove there is minimal droppings. If they find some then cut all cells with rebar. Is this partially grouted? Or go straight to check all the cells that have bar. What is your comfort level... at this point they bear the responsibility to prove it will work so put as much of a burden on them as necessary to prove out the design.
 