NDS section 4.1.5 states: Wood-frame shear walls, wood-frame diaphragms, trusses, and other wood members and systems shall not be used to resist seismic forces contributed by masonry or concrete walls in structures over one story in height.
The exceptions are as follows:
1. Wood floor and roof members shall be permitted to be used in diaphragms and horizontal trusses to resist horizonal seismic forces contributed by masonry or concrete walls provided such forces do not result in torsional force distribution through the diaphragm or truss.
2. *Summarized* - limit to 2 stories provided that floor to floor heights do not exceed 12', diaphragms shall not be considered to transmit forces by torional force distribution or cantilever past the outermost supporting shear wall, diaphragms shall be blocked, 15/32" min sheathing on shear walls & blocked, no out of plan horizontal offsets between stories of shear walls.
I am curious how others view these statements as I have seen many apartment and other buildings buildings that are taller than 3 stories, wood framed and have the masonry cores tied into the lateral system, per these code requirements, I don't see how it's possible to justify dragging the masonry into the wood system when taller than 2 stories and "meet code".
The solutions I keep coming back to are as follows:
1. Design the cores as standalone structures and have a seismic joint all around - architects hate this.
2. Design the cores as standalone structures and "box out" with beams around the structure, but run the sheathing past the members and butt against the core and rely on the floor sheathing being a weak point that may fail/crack during an event.
3. Wood cores - not all contractors have come around to this thinking yet and like that the masonry/concrete cores can be considered OSHA access as well during contruction.
Going one step further, would it be permissible to use a lower R value (of the masonry or concrete system) and design the wood and masonry together, this appears to be a common approach per Structure Magazine and WoodWorks publications, however it doesn't appear that this meets the requirements of the NDS code as technically you are still relying on wood shear walls to offer some resistance to the seismic forces contributed by the Masonry/Concrete cores. What are your thoughts? Are there any other good publications/information on this issue?
The exceptions are as follows:
1. Wood floor and roof members shall be permitted to be used in diaphragms and horizontal trusses to resist horizonal seismic forces contributed by masonry or concrete walls provided such forces do not result in torsional force distribution through the diaphragm or truss.
2. *Summarized* - limit to 2 stories provided that floor to floor heights do not exceed 12', diaphragms shall not be considered to transmit forces by torional force distribution or cantilever past the outermost supporting shear wall, diaphragms shall be blocked, 15/32" min sheathing on shear walls & blocked, no out of plan horizontal offsets between stories of shear walls.
I am curious how others view these statements as I have seen many apartment and other buildings buildings that are taller than 3 stories, wood framed and have the masonry cores tied into the lateral system, per these code requirements, I don't see how it's possible to justify dragging the masonry into the wood system when taller than 2 stories and "meet code".
The solutions I keep coming back to are as follows:
1. Design the cores as standalone structures and have a seismic joint all around - architects hate this.
2. Design the cores as standalone structures and "box out" with beams around the structure, but run the sheathing past the members and butt against the core and rely on the floor sheathing being a weak point that may fail/crack during an event.
3. Wood cores - not all contractors have come around to this thinking yet and like that the masonry/concrete cores can be considered OSHA access as well during contruction.
Going one step further, would it be permissible to use a lower R value (of the masonry or concrete system) and design the wood and masonry together, this appears to be a common approach per Structure Magazine and WoodWorks publications, however it doesn't appear that this meets the requirements of the NDS code as technically you are still relying on wood shear walls to offer some resistance to the seismic forces contributed by the Masonry/Concrete cores. What are your thoughts? Are there any other good publications/information on this issue?