boffintech
- Jul 29, 2005
- 469
Aggregate for grout is required to conform to the grading requirements of ASTM C-404, Table 1. The table shows that for course aggregate, #8 stone and #89 stone, 100% of the material is passing the 1/2" sieve. Therefore one can conclude that the largest size stone allowed in course course aggregate is 3/8".
Today I read over a mix design submittal from LaFarge on an Agilia mix that they refer to as "Block Fill". Interesting phraseology: "Block Fill" not "grout", but I digress.
The mix design is basically blank, but it comes with a letter explaining that the mix is proprietary, that they spent millions of dollars inventing it, and that they aren't going to give up the mix proportions.
OK, whatever, my real beef is with the following...
The letter goes on to state:
1) that the mix "meets ASTM C-476-02 standard specification for course grout masonry"
2) that the "nominal size aggregate 1/2 inch".
Isn't this letter in error? Reason: C 476 section 3.1.3 reads "Aggregates shall conform to Specification C 404." And C 404, Table 1 shows zero material on the 1/2" sieve.
And BTW, the letter is further in error because the name of C 476 is "Standard Specification for Grout for Masonry", not "Standard Specification for Course Grout Masonry."
Who is correct?
Who is correct?