What is the maximum size (length) opening you would allow in Masonry without at Lintel?
The specifics are:
- Clay (brick) masonry load-bearing walls (3 or 4 wythes thick). Old historic building, early 1900's.
- Interior bearing walls (2 storey building with wood floors & roof)
- Penetrating walls with various size ducts
Obviously 1 to 2" diameter pipe is no issue, but there are duct openings ranging from 8" to 48" wide. The larger openings (24" to 48") will get Steel Lintels for sure, but the 8" to 12" range, I am unsure.
I looked briefly thru BIA Tech notes & ACI 530 and couldn't find anything. In Masonry Designers Guide (2nd Ed), Section 15.4.8 says >12" needs a lintel and references a Code Section 9.9.1 (which is old ACI 530-95, and there is no such section in ACI 530-08).
The specifics are:
- Clay (brick) masonry load-bearing walls (3 or 4 wythes thick). Old historic building, early 1900's.
- Interior bearing walls (2 storey building with wood floors & roof)
- Penetrating walls with various size ducts
Obviously 1 to 2" diameter pipe is no issue, but there are duct openings ranging from 8" to 48" wide. The larger openings (24" to 48") will get Steel Lintels for sure, but the 8" to 12" range, I am unsure.
I looked briefly thru BIA Tech notes & ACI 530 and couldn't find anything. In Masonry Designers Guide (2nd Ed), Section 15.4.8 says >12" needs a lintel and references a Code Section 9.9.1 (which is old ACI 530-95, and there is no such section in ACI 530-08).