smvk3
Structural
- Mar 1, 2014
- 57
I have a project where I am using #6 and #7 rebar for an 8" CMU wall. The design code is 2006 IBC and the required masonry rebar lap splice length is 72d[sub]b[/sub] due to the stress in the bars. So for a #6 and #7 bar, the required lap splice length is 54" and 63", respectively.
The masonry contractor wishes to construct the wall in 48" lifts. I have a note on the drawings stating that the lap splice shall be within the grouted lift height for the wall, otherwise rebar couplers would have to be used. Therefore, the contractor would have to increase the height of his lifts from 48" to at least 56" for walls reinforced with #6 bars, and 64" for bars reinforced with #7 bars.
The contractor stated I am wrong and that the splices dont need to be within the grouted lift of the wall. However, I dont see how this would work as you could have up to three bars in one area due to overlapping splices.
Is the contractor right?
The masonry contractor wishes to construct the wall in 48" lifts. I have a note on the drawings stating that the lap splice shall be within the grouted lift height for the wall, otherwise rebar couplers would have to be used. Therefore, the contractor would have to increase the height of his lifts from 48" to at least 56" for walls reinforced with #6 bars, and 64" for bars reinforced with #7 bars.
The contractor stated I am wrong and that the splices dont need to be within the grouted lift of the wall. However, I dont see how this would work as you could have up to three bars in one area due to overlapping splices.
Is the contractor right?