Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Masonry Shear Wall Section Modulus

Status
Not open for further replies.

mnovicki

Structural
Feb 4, 2008
13
Can anyone direct me to a quick and dirty way to calculate and/or reference the section modulus (or moment of inertia) of a masonry wall not fully grouted (say 32" o.c.) for in plane bending.....?

 
Replies continue below

Recommended for you

You can use the EST (Equivalent Solid Thickness) for you "b" value, so it is like calculating the section modulus of a rectangle.

For 8" masonry with cells grouted at 32" c/c the EST would be 4.9". I got this value from the Reinforced masonry Engineering Handbook by James Amrhein
 
mnoviki-

The suggestion of Jim Amrhein's book is very good for an analytical approach. Unfortunately, Jim died several years ago, but his great work is sound from a professional and practical standpoint, but some codes and ACI 530 have made a few changes.

The NCMA TEK Notes are very sound and are written by very kowledgable professional enginers (educated by Jim Amrhein's books), but participation on all of the major national and international code and materials stadards (ASTM, ACI, TMS, etc.).

Go to the NCMA for current interpretations, but do not ignore Jim Amrhein's insight into the industry.

Dick
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor