Looking at designing a load bearing, masonry wall in a high wind area. Wind Load is 37psf, wall is 17' tall. For the sake of simplicity for my question, I'm treating the roof load as negligible and only using wind loads.
Going through the TEK manual, I get a #5 @ 24" o.c. from the allowable stress design tables.
**16,039lb-in/ft required, 16,420lb-in/ft provided
When I do strength design per ACI530...I get (without any reductions, yet)...33,374lb-in/ft provided. The formula I used is Mn=(Asfy)(d-(a/2))
I thought maybe instead of fy=60,000psi, I should've used Fs=24,000psi but that yields 14,118lb-in/ft. Do the 2 methods yield these drastically different results or have I made a mistake? I also cannot seem to "back calculate" the allowable stress tables.
Thanks for the attention. JEW